Hello together,
as you can see in my screenshots the LANSWEEPER dosen't report any alert massage.
On the UPS webserver I can see it without any Problem. What can I do ?
as you can see in my screenshots the LANSWEEPER dosen't report any alert massage.
On the UPS webserver I can see it without any Problem. What can I do ?
Labels:
- Labels:
-
General Discussion
1 REPLY 1
Options
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
‎08-28-2017 01:02 PM
The information in the BatteryStatus field on the asset page of this UPS is directly retrieved from SNMP of the device in question, so I assume the OID from which the battery information is retrieved is still returning a normal "BatteryStatus". If a rescan still yields a normal BatteryStatus this means that the APC UPS isn't updating every field related to its battery to reflect that one of the batteries is faulty, as Lansweeper is merely reading out what it finds.